Search for tools and product advice,
Discuss borrowed neutral in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
i=p/u
only on level 2330-5, could anyone shed some light on borrowed neutrals, as i dont know about them? thanks for your input. im guessing its using a neutral from different circuits and to do with old installations..
pretty much as you say, most commonly found on lighting at stairs
normally a live link between the commons of the two way switch downstairs and the neutral is picked up from the upstairs lighting
as it stands it wont cause concern until an rcd is introduced which will detect the imbalance and trip
Dilema is that if you pull the fuse on ckt 2 to add a new light it can be shown to be dead.
You disconnect the neuteral on ckt 2 for some reason and someone turns on the light with the shared neutral and that would wack 240V onto the "neutral" in your hand and ...
Domestically it would be twin and earth but if you only isolated the one circuit at the consumer unit and disconnected the neutral anywhere then the whole circuit (well the bit that is disconnected from the DB neutral) would be live, you might never know that it had been done. For instance you are fitting lounge ceiling rose and someone turns the upstairs light on then you are working live!
For reference Regulation
314.1 Every installation shall be divided into circuits, as necessary, to:
vi ) Prevent the indirect energizing of a circuit intended to be isolated
314.4 Where an installation comprises more than one final circuit... for each circuit the wiring shall be electrically separate from that of every other final circuit, so as to prevent the indirect energizing of a final circuit intended to be isolated.
Reply to borrowed neutral in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Hi folks I've just identified as cause of lighting circuit tripping in consumer unit a low volts ceiling light with laride transformer taking in...