only on level 2330-5, could anyone shed some light on borrowed neutrals, as i dont know about them? thanks for your input. im guessing its using a neutral from different circuits and to do with old installations..
 
pretty much as you say, most commonly found on lighting at stairs

normally a live link between the commons of the two way switch downstairs and the neutral is picked up from the upstairs lighting

as it stands it wont cause concern until an rcd is introduced which will detect the imbalance and trip
 
Last edited by a moderator:
electrics:safety_information:borrowedneutral18be.jpg
 
Dilema is that if you pull the fuse on ckt 2 to add a new light it can be shown to be dead.
You disconnect the neuteral on ckt 2 for some reason and someone turns on the light with the shared neutral and that would wack 240V onto the "neutral" in your hand and ...
 
Last edited:
Domestically it would be twin and earth but if you only isolated the one circuit at the consumer unit and disconnected the neutral anywhere then the whole circuit (well the bit that is disconnected from the DB neutral) would be live, you might never know that it had been done. For instance you are fitting lounge ceiling rose and someone turns the upstairs light on then you are working live!
 
For reference Regulation
314.1 Every installation shall be divided into circuits, as necessary, to:
vi ) Prevent the indirect energizing of a circuit intended to be isolated

314.4 Where an installation comprises more than one final circuit... for each circuit the wiring shall be electrically separate from that of every other final circuit, so as to prevent the indirect energizing of a final circuit intended to be isolated.
 
Last edited:

Reply to borrowed neutral in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
650
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
647
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
535
Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...
Replies
3
Views
590

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock