Discuss EICR coding of 521.8.1 violations (3P over 2 cables) in the UK Electrical Forum area at ElectriciansForums.net

pc1966

Esteemed
Arms
Reaction score
11,933
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited the "opposite" issue of a 3P circuit spilt over two T&E runs. Yes, I know that is bizarre and not something you really would expect to meet. However, that got me wondering how would you code this in an ECIR?

It seems less of a risk than the "borrowed neutral" C2 installation fault, after all you commonly see two or more cables run from the same MCB for, say, lights or a RFC split as the least-worst fix, etc, so having to verify the isolation of each and every cable you are working on is normal.

So while not a good indication of skill in installation, C3 would appear to be the obvious coding. Any thoughts?
 
I think I'd be giving that a C3, too. When you read the full 521.8 section it has no issue with multiple conductors in parallel, individual phases run as singles and so on, or multiple ciruits in the one cable - it just asks that you do one or the other, not mix and match! So therefore it would be an infringement that needs improvement rather than being a tangible risk to a person of BA1. This is also why we teach safe isolation of every conductor to every conductor, not just "yeah, the brown one's dead...."
 
How old is the T&E and what is it's maximum working voltage rating?

Over the years there has been T&E which does not have a suitable working voltage rating for 3 phase, which would be a C2 in my opinion.
 
How old is the T&E and what is it's maximum working voltage rating?

Over the years there has been T&E which does not have a suitable working voltage rating for 3 phase, which would be a C2 in my opinion.
That's fair enough, but in terms of the OP, where do you stop the metaphorical ball of string - Method? Unsupported spans? Terminations..... etc.
 
Nobody is going to expect 400v between cores in a t&e although Prysmium website states a nominal voltage of 300V or 500V for 6242Y cable
Maybe the Spanish Inquisition would do?

It is odd that the vast majority of 3&E cable is used for two-way switching on SP circuits even though the cable is colour coded for use as a 3P+E cable.
 
How old is the T&E and what is it's maximum working voltage rating?

Over the years there has been T&E which does not have a suitable working voltage rating for 3 phase, which would be a C2 in my opinion.
I would be surprised if T&E is not able to deal with the 3P voltages as each core is rated to at least the nominal Uo to earth, and as that is between conductors they see nothing different. Even between the two lives on one side of the CPC in 3&E cable there is now double the thickness of primary insulation, and so something getting towards double the breakdown voltage (not double as I doubt the electric fields are uniform, etc).

But you are certainly right this is a C2 circuit but for many reasons:
  • Violation of regulation 521.8.1 on splitting a circuit over multiple multi-core cables = C3 (agreed?)
  • The pair of T&E cables are run together, clipped direct, and not in any path of likely damage = no code, good!
  • Cables painted multiple times with oil paint (AFIK) probably leading to degraded outer sheath = C3 ?
  • Use of 1mm cable on a power circuit, was C3 but now permitted by regs so no code.
  • Protection is by means of (as far as I could judge) 20A fuse wire in BS3036 holders shared with other circuits = C3 as it might meet adiabatic (not checked Zs), but fails to provide overload protection against a jammed motor or loss of one phase since no signs of any motor protection (e.g. proper starter, etc)
It is not any of my professional business as such, but it is not something I am happy seeing continue anywhere, let alone a friend's property now.
 
I would be surprised if T&E is not able to deal with the 3P voltages as each core is rated to at least the nominal Uo to earth, and as that is between conductors they see nothing different. Even between the two lives on one side of the CPC in 3&E cable there is now double the thickness of primary insulation, and so something getting towards double the breakdown voltage (not double as I doubt the electric fields are uniform, etc).

But you are certainly right this is a C2 circuit but for many reasons:
  • Violation of regulation 521.8.1 on splitting a circuit over multiple multi-core cables = C3 (agreed?)
  • The pair of T&E cables are run together, clipped direct, and not in any path of likely damage = no code, good!
  • Cables painted multiple times with oil paint (AFIK) probably leading to degraded outer sheath = C3 ?
  • Use of 1mm cable on a power circuit, was C3 but now permitted by regs so no code.
  • Protection is by means of (as far as I could judge) 20A fuse wire in BS3036 holders shared with other circuits = C3 as it might meet adiabatic (not checked Zs), but fails to provide overload protection against a jammed motor or loss of one phase since no signs of any motor protection (e.g. proper starter, etc)
It is not any of my professional business as such, but it is not something I am happy seeing continue anywhere, let alone a friend's property now.
Genuinely interested to hear your thinking on how a multiple occurrence of C3’s adds up to a C2. I think from what you say here that there is actually a C2 (1mm line conductor on a 20A OCPD??) but unless I’m reading it wrong after a vino or two (or is a typo) you’ve suggested as a C3. As an aside, I remember having a discussion on a thread on here about painted cables with Lucien and the conclusion was that it made no tangible difference.
 
Genuinely interested to hear your thinking on how a multiple occurrence of C3’s adds up to a C2. I think from what you say here that there is actually a C2 (1mm line conductor on a 20A OCPD??) but unless I’m reading it wrong after a vino or two (or is a typo) you’ve suggested as a C3. As an aside, I remember having a discussion on a thread on here about painted cables with Lucien and the conclusion was that it made no tangible difference.
Yes, last one ought to be C2 from BPG#4:

Circuits with ineffective overcurrent protection (due, for example, to oversized fuse wire in rewireable fuses)

However, it has been mentioned before that an "unsatisfactory" judgement could be based on a lot of poor C3 factors combined, rather than one blindingly obvious C1/C2 fault in the design/installation. Methinks that is another thread that could run and run!
 
. As an aside, I remember having a discussion on a thread on here about painted cables with Lucien and the conclusion was that it made no tangible difference.

The only time I've seen it make a noticeable difference was in a farmhouse where lord knows what had been painted on the exposed beams and it had eaten into some of the old surface run T&E.
 
The only time I've seen it make a noticeable difference was in a farmhouse where lord knows what had been painted on the exposed beams and it had eaten into some of the old surface run T&E.
At a guess I'd say original Creosote. That stuff was nasty!!
 
Creosote will degrade PVC, but used on beams inside a house? That stuff stinks.
True. Although I'd hazard a guess that things like woodworm treatment are probably chemically quite similar? Don't know.
 

Reply to EICR coding of 521.8.1 violations (3P over 2 cables) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
594
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
804
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...
Replies
14
Views
3K
Hi, Currently undertaking an EICR on a factory, we have came across an 4 core SWA and 4 Core SY which have been split in the DB to serve two...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock