Hi guys, sorry for asking a dumb --- question but I just started to test new builds after a 7 year absent. I always known Circuit Breakers in a domestic CCU as BS60898. But some one looking at my paper work today said that I was using the wrong number. I passed my 17th about a year ago a don't recall there being any change. Can some one clear this up for me?.
regards
:smilewinkgrin:
regards
:smilewinkgrin:
How old was the board you were testing?
There are different BS numbers for OCPDa which should be visible on them, that's what should be recorded on a cert not just a generic number you think is correct. The reason being the max Zs values vary between them.
regards
:smilewinkgrin:
Read the bs number written on the circuit breaker and then write it in the box on the certificate.
regards
:smilewinkgrin:
Chill out mate, you've gone back in time.
They're 3871s! :smilielol5:
Current domestic MCBs should be BS EN 60898.
Industrial MCCBs BS EN 60947-2
However if they are RCBOs then they are BS EN 61009.
That's what I thought, I'll ignore all the ---- posts on here. why do I need to look at a number when I all ready know it. My post was simply asking had there been a recent update to the regs changing these breaker as all my books still say that the 60898 is valid.
Not looking at the info on the ocpd's will bite you in the backside. Did you assume the KA ratings and current ratings also.
How do you know you have put the correct info if you haven't actually looked at the device itself?
It is obvious from some of the replies that some of the posters lack real experience.
and the trolls are out.
sado
So you carry out verification by assumption mmmm!! so what other assumptions do you make when filling in the cert
You are obviously making observations of yourself with the comment you have made as someone with "real experience" would not have needed to start this thread so who is the real sado
15 All!
If you take the time to read the post you will see that what I was asking was if the number had been changed nothing more. I think only one poster actually bothered to answer the question. I have no idea what the rest of you a banging on about.
Apart from the fact that you are obviously are trolls and have nothing better to do with your time but to look for post hoping you might get an opportunity to put someone down.
Peter, stop throwing your teddies out of your pram!
Edit: I asked you a question in post #2 and you didn't answer!
You asked if the number which is written on every breaker has changed, bearing in mind you will have checked the number on the breaker as part of the inspection to confirm that the correct breakers have been fitted.
Why do you think people didn't take you seriously?
No one has "trolled" on this thread. All we have done is pointed out a error in your method of filling it a cert and the lack of looking for the CORRECT information to put in the relevant box. Seems you have a problem accepting criticism.
regards
:smilewinkgrin:
bs60898 is for sp mcb's
the 100a dp main switch is BS EN 60439-3
So Cazmac1 reading your original post
regards
:smilewinkgrin:
Did the person looking at your paperwork go to site to verify this, if you had done your inspection correctly your answer would have been "that was the BS number printed on the MCB"
The only ---- posts are yours they are full of $$$$
Even if the regs had been updated you still use the BS number printed on the MCB
The art of using your eyes
We take the time to read your post and reply and we are trolls yet you slag other posters off for your own failing of not being able to back up your test sheets because you didn't check the BS number printed on the MCB
Correct one person quoted the current BS numbers so because they are the current BS numbers you have ASSUMED that is what is fitted
Because you are using the same verification and observation system that you use on site when doing inspections to read these USEFUL posts
As this thread is of little use to anyone who carries out proper I&T you are the original troll with the original post
I hope this and the useful other posts in this thread will help you improve your I&T skills and remember the BS number printed on the MCB is the one you use
So back to the OP, if it a brand new CU then the choices are probably 60898 or 61008 - but then what do I know - or more to the point what do you know?
Bs 60898
Thread Tags
Tags Tags
None
Cazmac1,
Octopus,