Afternoon....

I have just completed an EICR and am unsure if the Wylex BS3036 fuses require a code due to their breaking capacity related to the PFC.

Firstly I would like to identify if they are S1A, S2A or S4A as that would solve the problem of the PFC being 1.35kA, however I dont think its going to be possible to identify them as there are no markings indicating this information.

So I will put 1kA for breaking capacity which is < PFC!

Guidance note 3 says that you can take the s/c capacity of the fuses to be 16KA when:

the current ratings of the devices don't exceed 50A
The d/b is a 5486-13 or better
it is supplied through a type 2 BS1361 fuse rated at no more than 100A

But if the above is acceptable then I cant quite see the point in having a breaking capacity rating on fuse/MCB if we are going to ignore it?

Do most of you accept GN3 and would not be concerned? Or would you want to change for MCB's with a higher breaking capacity?

I have to admit I do not have a copy of GN3 so have just found the above paragraph on the internet, if I had the copy in my hand and could read it thoroughly I would find it easier to make a decision.
 
Last edited:
are you ready to carry out EICR's when you still have to come on the forum every day to get help with all your jobs ?

sorry but inspections require a level of experience you do not possess.
 
To be fair to hhd he has researched for a answer before asking unlike some on here. He has also shown he is capable of thinking outside the box a little bit, I am sure we have all had to look up these sort of things before.

Has he got the experience and knowledge to carry out a EICR I dont know bit at least he seems to be attempting to do it properly rather than just guessing his way through it.
 
To be fair to hhd he has researched for a answer before asking unlike some on here. He has also shown he is capable of thinking outside the box a little bit, I am sure we have all had to look up these sort of things before.

Has he got the experience and knowledge to carry out a EICR I dont know bit at least he seems to be attempting to do it properly rather than just guessing his way through it.

well thats just fine & dandy , but the customer could have been handed a report recommending replacement of his rewirables for no other reason than theres no PSC rating on the side of the fuse carrier.

and in my mind 3036's will deal with 3kA fault current all day long...........
 
see your comment, dilb, and agree. HHD has shown his dedication to the trade and, although having come in through the Electrical Trainee route, is keen to get it right and deserves all the help we can give him, respect.
 
Guidance note 3 says that you can take the s/c capacity of the fuses to be 16KA when:

the current ratings of the devices don't exceed 50A
The d/b is a 5486-13 or better
it is supplied through a type 2 BS1361 fuse rated at no more than 100A

But if the above is acceptable then I cant quite see the point in having a breaking capacity rating on fuse/MCB if we are going to ignore it?

Do most of you accept GN3 and would not be concerned? Or would you want to change for MCB's with a higher breaking capacity?

I have to admit I do not have a copy of GN3 so have just found the above paragraph on the internet, if I had the copy in my hand and could read it thoroughly I would find it easier to make a decision.

As you say, if the upstream BS1361 has a high enough breaking capacity, then you don't need to worry. :)

Always worth noting it on the report though.
 

Cheers Trev,
But that still shows the breaking capacity could be anywhere from 1-4kA which makes quite a difference with a PFC of 1.35kA.

You need to put N/V (not verified) for the Ka rating of the OCPD if its not present. Then code it accordingly on your report.

It's a difficult one to code Dillb.. I think it's potentially dangerous as PFC > breaking capacity but GN3 states otherwise.

are you ready to carry out EICR's when you still have to come on the forum every day to get help with all your jobs ?

sorry but inspections require a level of experience you do not possess.

Yes.

1.1 threads started p/week..... daily? I do get picky about inaccurate statistics!!!!

But thanks for the input :-)
 
Last edited:
well thats just fine & dandy , but the customer could have been handed a report recommending replacement of his rewirables for no other reason than theres no PSC rating on the side of the fuse carrier.

and in my mind 3036's will deal with 3kA fault current all day long...........

Thats a fair point..

Which page is that on Biff? :smile5:

edit ..................

sorry, that was a bit cheeky! Couldn't resist!
 
Last edited:
To be fair to hhd he has researched for a answer before asking unlike some on here. He has also shown he is capable of thinking outside the box a little bit, I am sure we have all had to look up these sort of things before.

Has he got the experience and knowledge to carry out a EICR I dont know bit at least he seems to be attempting to do it properly rather than just guessing his way through it.

HHD knows how to get the best out of the forum by offering up problems, his ideas of solutions, answering questions and giving feedback.

He could teach the majority of new posters a thing or 2 about forum etiquette!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
BS3036 breaking capacity and PFC..
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
31
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Lucien Nunes,
Replies
31
Views
14,087

Advert

Back
Top