Main problem with the observations, is that they are badly worded.
Observation 1 for instance:
There is no requirement for there to be an earth between the metal front to the back box.
There is a requirement to earth exposed conductive-parts, which the back box could arguably be considered as such (if it’s metal).
As such the observation should be metal back boxes not earthed (or something similar).

Observation 4 is something that would be expected, because the cables would be longer. Not in itself an issue.

Observation 5 is not an issue.

Observation 11.
There are 3 voltage bands:
ELV (up to 50V), LV (50V to 1000V) and HV (above 1000V).
So to say that the voltage is not LV, means it is either ELV (good), or HV (very bad and also very unlikely).
The lack of earth may well be because the fitting is double insulated.

There’s quite a few there that are not issues, and some which are issues, but not necessarily related to the work conducted in 2005 and 2007.
 
By ******** - do you mean they're all minor issues, or actually not coded up the correct way, or in fact both?

A bit of both tbh..
Also in the test schedule the Zs values for sockets look dubious..

I find EICRs like this very frustrating, they are used as a legal document, a tool for knocking thousands off the price of houses, so come on let’s at least do a proper professional job of them
 
A very contentious report I must say

There is one obvious deficiency that can be agreed by all
There is a blank missing at the consumer unit o_O
 
A bit of both tbh..
Also in the test schedule the Zs values for sockets look dubious..

I find EICRs like this very frustrating, they are used as a legal document, a tool for knocking thousands off the price of houses, so come on let’s at least do a proper professional job of them
It's ok in our case we're not knocking £1000s off for this report.
 
Thanks for your replies. Much appreciated. It would - on a general level - be quite interesting to get 3 electricians to do an EICR on the same property and see what was / wasn't picked up. Not as a finger-pointing exercise but simply to see what different interpretations or focuses there may be.
 
Thanks for your replies. Much appreciated. It would - on a general level - be quite interesting to get 3 electricians to do an EICR on the same property and see what was / wasn't picked up. Not as a finger-pointing exercise but simply to see what different interpretations or focuses there may be.
Anyone want to do this in Sheffield in a couple of months time let me know :D
 
seems like there's a HV shower light? and missing blanK??? i'd have just put one in.
 

Reply to Building control / works certificate in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock