There are two immersion heaters in one insulated tank. The first is a Heatrae Centerbrand Superloy 800 and is 2.8kW @ 230V. The other is a Backer 2.7kW @ 230V.
The owner was told that evening and I disconnected one of the immersions. I then replaced the burnt neutral with a new tail and terminated it to one of the non-melted points as a temporary, safe fix. The EICR has amongst over 20 other observations, a C1 for this....obviously!
A replacement 7671-3 CU is going to be done. I'll also run the immersions on an indep circuit protected with a 20A breaker as will the oven.
No - the outer sheathing had melted and globbed down the conductor.
Yes - the R1-R2 were fine but rubbish / null IR readings which is a real head-scratcher and I'd welcome any sensible avenues of investigation.
 
There are two immersion heaters in one insulated tank. The first is a Heatrae Centerbrand Superloy 800 and is 2.8kW @ 230V. The other is a Backer 2.7kW @ 230V.
The owner was told that evening and I disconnected one of the immersions. I then replaced the burnt neutral with a new tail and terminated it to one of the non-melted points as a temporary, safe fix. The EICR has amongst over 20 other observations, a C1 for this....obviously!
A replacement 7671-3 CU is going to be done. I'll also run the immersions on an indep circuit protected with a 20A breaker as will the oven.
No - the outer sheathing had melted and globbed down the conductor.
Yes - the R1-R2 were fine but rubbish / null IR readings which is a real head-scratcher and I'd welcome any sensible avenues of investigation.
Can you explain the last paragraph in greater detail? R1+R2 were fine but rubbish/null IR readings?????
 
To cover you behind send the customer a Danger Notice without delay. It looks too far gone to be cured by tightening the screw up. What do you mean by IR is open circuit (OC) ?, if it is how have you got satisfactory r1+r2 ? You have what is known as "guilty knowledge" of a potential fire risk. Ideally tell them it must be isolated and the C.U. replaced immediately, I realise that may not be practical, so send the Danger Notice and make it their problem not yours ! Sorry if I sound like an arse but where there's a blame, there's a claim !! .

I wouldn't rely too much on this 'danger notice' to cover your arse, I think it is more likely to be used to prove that you left a known danger in place rather than help you get away with it if the worst did happen.
Don't forget that this 'danger notice' (if you are referring to what I think you are) is something invented by the nic which has no basis in the regulation or law.
 
There are two immersion heaters in one insulated tank. The first is a Heatrae Centerbrand Superloy 800 and is 2.8kW @ 230V. The other is a Backer 2.7kW @ 230V.
The owner was told that evening and I disconnected one of the immersions. I then replaced the burnt neutral with a new tail and terminated it to one of the non-melted points as a temporary, safe fix. The EICR has amongst over 20 other observations, a C1 for this....obviously!
A replacement 7671-3 CU is going to be done. I'll also run the immersions on an indep circuit protected with a 20A breaker as will the oven.
No - the outer sheathing had melted and globbed down the conductor.
Yes - the R1-R2 were fine but rubbish / null IR readings which is a real head-scratcher and I'd welcome any sensible avenues of investigation.

Only the lower heater should be connected in a two immersion heater cylinder if no off-peak/E7 supply is available.
The upper heater is only there to be a boost element in an off-peak/E7 setup. It will do little to no work if it is switched on at the same time as the lower heater, the heat from the lower heater will quite quickly operate the thermostat of the upper heater and switch it off. Also with modern immersion heaters the lower element can operate the overheat trip of the upper element and switch it off permanently (until reset)

Why are you quoting the 230V power ratings? The public electricity supply in the U.K. is 240V, the mythical 230V only exists on paper and not in the real world. These immersion are will be operating at 3kW and using the lower power ratings will lead to you designing and installing a circuit with a small overload which is a dangerous situation.

What is a rubbish/null IR reading? All of the IR testers I have used have only ever had a numerical scale so I haven't a clue what those readings equate to.
 

Reply to Burnt Main Downstream Neutral in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
679
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K
I'm having an extension built and the builder leading the project has said that the electrician will be over in about 4-6 weeks to start his works...
Replies
4
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock