P

Penney

A plumber has installed a 8.3kw heating boiler pulling 35a which is being fed from a 6mm . it has burnt two 45a cooker switches already. Why. Rewiring to 10mm will be hard as tenants just moved in. Owner going mad ! Cable is running above ceiling near downlighters and poss insulation. Also could be bunched. What are my options. Help.
 
first check cable run and calclulate if 6mm will cope with 35A. clipped direct is 47A so you have a certain derating to play with. second, are the switches good quality and are the terminations good? at a push, you could do away with the switch and use the MCB for isolation.
 
Poor quality switches, and / or poor quality fitting of the switch.
Buy a switch that has 2 screws for each terminal, you'll get a good connection then, and hopefully it wont happen again.
 
Firstly, blame the plumber who installed heating boiler, without reference to the design of the electrical supply cable. Who installed the 6m cable or was it an existing cable (looking to blame someone else). Then present the options to the home owner, with the blame not apportioned to you.
 
Firstly, blame the plumber who installed heating boiler, without reference to the design of the electrical supply cable. Who installed the 6m cable or was it an existing cable (looking to blame someone else). Then present the options to the home owner, with the blame not apportioned to you.

We don't know that it needs 10mm cable do we? Daz
 
look in definitions for bugger". maybe not in BS7671, you might find it in the Vatican Priests' handbook.
 
Can we all stop saying 'bugger' please. It's not on. Daz
 
I've seen it happen a few times where the first switch has a loose connection causing it to burn out.
Then a muppet comes along to replace the switch but doesn't cut the burnt bit of conductor off and it causes another overheated connection
 

Reply to Burnt out switches in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
15
Views
378
Hi Guys After bit of advice please.... Called back to kitchen job today, Hamilton light switch we fitted has burnt out?! Normally decent gear so...
Replies
24
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
786
Hoping someone can give some input on what could be possible causes of what happened here. I am going to investigate the situation next week but...
Replies
27
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
15
Views
534

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock