Discuss Cable calc advice needed... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

G

Gottssam

Hi there,

Have just picked up a job to price and i'm struggling to work out the best solution to the problem. Any help would be greatly appreciated.

Scenario.... Large 5 bed house being split into 5 rooms for separate rental. Landlord has decided to install 5 power showers to each of the individual en-suites. I have advised him to go for 8.5kw showers to keep the load down.

There is also a mini-kitchen going into each room with a washing machine, oven (fan assisted) kettle, microwave etc.

I planned to install a 10 way RCD split load consumer unit with 5 40amp MCB's for the showers and 5 32amp MCB's for the kitchens. After applying diversity, i still have a maximum demand of over 100amps. Does it matter that there's only an 80amp 1361 main fuse? There is also already another cu with a few rings, lighting circuits etc from it.

Only just came out my time recently so still earning as i go. Any info/guidance would be great.

Cheers
 
The showers alone will be over 180A - no diversity allowed. This installation will require a 3 phase supply, something the landlord will have to pay for before you even contemplate carrying out any work.
 
When you say power shower i take it you mean an electric shower with heater element as a power shower to me is a hot and cold fed shower with an electric pump that uses practicaly no juice.
 
Sorry, i meant cold water fed, element heated showers (8.5kw).

I figured that this type of shower fell under "instantaneous water heater" in App1 of IEE OSG? Which states 100% of full load of first two, then 25% of remaining. Even still though that is over the 80amp main fuse. So am i correct in assuming my maximum demand after applying diversity needs to be within the 80amp main fuse rating?

Thanks for your help
 
You are correct in what you say with allowance for diversity. But these are 5 separate dwellings so personally i would not allow diversity as the showers could be used at the same time.

No you are not correct, the main fuse should be of sufficient rating without diversity applied.
 
Last edited by a moderator:

Reply to Cable calc advice needed... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
668
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hello All Strange question for you, I know you don’t have crystal balls :) but can anyone give me any clue on the following… I have mid eighties...
Replies
8
Views
1K
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K
Hi Pretty new here, so not sure if this question goes into this thread I am not an electrician; however, I plan to integrate IOT devices and...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock