wattsy

Evening all

Hopeully someone can help me get my head around this.

I'm looking at table 7.1 OSG. For the 1361/3036 45A radials on a TN-S system the limiting factor is sc, which means its limited by the line to neutral loop impedance (short circuit). But the TNC-S it isn't. Can't see what the difference between L - N fault on TNC-S and TN-S?

Can somebody please explain this to me in detail please i'm confused
Many Thanks
 
poss to do with the different values of Ze between TNS and TNCS. the Ze will influence your Zs
 

Reply to Cable length limit from table 7.1 in the Australia area at ElectriciansForums.net