Unwound the 25m reel was failing at 0.56 ohms. Before I started doing the maths to check !You can get extension reels in all sorts of length I see Screwfix selling a 45m one, from a reputable supplier. We have a rule of thumb that where the earth bond exceeds 0.18 ohm (I believe this equates to the suggested lengths in the CoP) that it is recommended it is only used with 30ma rcd protection, of course this does not take into consideration any volt drop issues.
Seaward Apollo 500 + I thought there was a built in calculator but couldn’t work it out on site. Have to read the manual again?What tester are you using? Some have settings for different length reels or a setting to put your own pass/fail value in if it's an odd length reel.
Are you talking about the RCD on the DB ??? They’re certainly not using a plug in RCD.You can't take them out of service for not having RCDs. The socket feeding them will more often than not have RCD protection.
Are you talking about the RCD on the DB ??? They’re certainly not using a plug in RCD.
Always wondered what the red button was for. ?
I'm pretty sure that's what is on my 50m cable reel, certainly not an RCD, I think its old enough that RCD's where not available back then.To be fair a lot of the red buttons are just overload reset buttons.
13A fuses have Zs limit of 2.3 ohms (Table 41.2) so assuming your supply Zs is around 1 ohm at the socket then if your cable R1+R2 is 1.3 ohm or less no problem?