A customer has bought a Rangemaster cooker 14.8kw, Rangemaster state the FLC is 55amps, cable wiring ref method is 100.............what cable breaker size should I use. This is for a domestic property?
Done diversity using the Kws / v, I'm really looking for someone to confirm what I have in my head or if I'm just mad!
Johnboy, I understand that and I believe that's why the cooker takes 55 amps and not 65 amps as 14.9kw / 230. Calculate diversity on the 65amps gives you 26.5amps. When I put all the above info into cable calcs, FLC 55, design current 26.5amps, install method 100 keeps telling me 16mm!