Just a quick question when taking cables across a public footpath I know the depth is 24 inch and all the relevant gravel and tape. But I can't get any deeper than 24 inch but there is a gas main and mains LV crossing my path. So essentially my ducting will be crossing there's do I need to separate these with any non combustible material. Thoughts?
 
Do you need permission from the Council to do this or is it a Public thoroughfare across somebody's property?
 
the standard depth is 450mm
no cables can be installed outside a private boundary without L.A. permission as all the utility drawings have to be updated to show your mains.
 
oh , and a few of inches of sand between cable and pipe will normally suffice as a barrier.
:-)
 
All permission granted I have all the drawings of utility's which is no problem as we have access to these.all ground cat and genny as we dig. All drawings will be updated when we are finished just the crossing of utilities is annoying me I want to go deeper but can't because of a layer of feels like kryptonite. 450 isn't deep enough we have to be at 600 min.

- - - Updated - - -

My problem is the more a put between them the further I raise it up. Very annoying,
 
450 across public footpaths? We have to be 600 for some reason. And I have to be honest the last 150 was the hardest!
 
Tell the blisters on my hands all about it. My hands aren't built for digging.

thats why God invented mini-diggers.
;-)

and no-ones gonna send round the gestapo cos you have to go shallower over obstructions.
you worry too much.
 
Because services are present it's a hand dig only! Crap rule that causes me pain! Seems like a lot of work for 4 lights!
 
Just a quick question when taking cables across a public footpath I know the depth is 24 inch and all the relevant gravel and tape. But I can't get any deeper than 24 inch but there is a gas main and mains LV crossing my path. So essentially my ducting will be crossing there's do I need to separate these with any non combustible material. Thoughts?

If you are Ducting, and that ducting is buried in soft sand throughout it's buried length and crossing points What on earth are you worried about?? Can't get much less a combustible material than sand now can you!! lol!!
 
Because services are present it's a hand dig only! Crap rule that causes me pain! Seems like a lot of work for 4 lights!

No it’s not. Once the services are located and uncovered by hand digging you can use power excavators so long as you have a watch man. (I think you lot refer to them as a banks man.)

I’ve run 11KV cables through solid rock to join or cross other live 11KV feeds in an existing trench.

When it comes to the trench bedding material, I found quarry sand to be the best. If it rains during the job it doesn’t run like building sand. Above the sand bed we used tiles followed by ¾” crusher run. (Ask the builders merchant.)
 