Hi again,
2.5 TE cable installed within fully insulated partition walls which i would of thought is now pretty mush standard now on new builds / refurbishments. According to OSG guide table F6 page 150 Ref method 103. 2.5mm cable down rated to 13.5 amps! Radial for imm/htr would be 16 amp breaker, therefore wrong, cable would have to have to be 4mm. Ring circuit double up. would on give 27amps, normally 32 amp breaker but in this case Breaker down to 20amp. Am i reading the tables correctly/
 
You're correct if you want to stick the cable down the centre of the insulation. As tel says, should be in contact with one side of the partition. If not possible, then you could always go with ref method A.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
England
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
Cables installed in insulated partition walls
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
driverman,
Last reply from
Guitarist,
Replies
5
Views
2,109

Advert

Back
Top