Discuss Calculating power factor with wattage and voltage in the UK Electrical Forum area at ElectriciansForums.net
Not unless you also know the current, from which to calculate the apparent power in VA.
pf = P/(V.I. sqrt(3)) as it's 3-phase
Suppose the line current were 21A, the power factor of your 13kW example would be
pf= 13,000 / (21x400xsqrt(3)) = 0.89
Reply to Calculating power factor with wattage and voltage in the UK Electrical Forum area at ElectriciansForums.net
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...