J

jan21

I have to calculate the total consumption for each of the circuits and state the final maximum demand current.

downstairs :2 fittings with 5x 12w lamps,1 fitting with 5 x 12w
1 fitting with 10 x 12w,1 fitting with 1 x 60w,1 fitting with 7 x 20w
2 fitting with 3 x 20w,1 fitting with 4 x 30w and 2 fitting with 1 x 20w,cooker 5.1kw

upstairs: 1 fitting with 5 x 12w,3 fitting with 1 x 20w,1 fitting with 1 x 60w, 1 fitting with 1 x 60w, 1 fitting with 1 x 60w, 1 fitting with 5 x 12w and 4 fitting with 1 x 20w. shower 9.8kw

Also , Upstairs: 10 sockets and Downstairs: 13 sockets and 4 fuses.

So far I've got:

Downstairs:

780w x1.8 / 240 = 5.85a

Kitchen cooker power consumption: 5100 w
x 1.8 / 240 = 38.25a
10a + 11.48a + 5a= 26.48
Upstairs
440w x 1.8 / 240 = 3.30a
Bathroom shower power consumption:
9800w x 1.8 / 240 = 73.5a
Upstairs: 10 sockets
100%X + 40%(Y+Z)

Downstairs: 13 sockets and 4 fuses
100%X + 40%(Y+Z)

13a13 - 60% = 5.2 = 13+5.2 = 18.2 seems wrong! ?
X is the full load current of the largest appliance or circuit
Y is the full load current of the second largest appliance or circuit
Z is the full load current of the remaining appliances or circuits
 
Re: calculating total consumption for each of the circuits and final maximum demand c

Welcome to the forum. Is this a college homework question?
 
Re: calculating total consumption for each of the circuits and final maximum demand c

Look up diversity in either OSG or BS 7671
 
Re: calculating total consumption for each of the circuits and final maximum demand c

What's the x1.8 for? Thought that 1.8 factor was only applied to discharge lighting?
 
Re: calculating total consumption for each of the circuits and final maximum demand c

he's other question is pretty good too!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
calculating total consumption for each of the circuits and final maximum demand curre
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
jan21,
Last reply from
flashh,
Replies
4
Views
2,691

Advert