This is all becoming much clearer to me so, so many thanks for the info. One thermostatic controller I know of has a 10A relay and the other a 16A relay... it now strikes me that the only reason the 40A relay is being used in the former is to boost its utility. In the latter, the 16A, it surely is not needed for a 3kw fire?
The way I come to this conclusion is by 3000w/240v= 12.5A - well within the 16A's capacity. Is this correct reasoning/maths?
What concerns me is that there is a controller out there with a 40A relay added, using 2.5mm cable, but with a 13A plug. How can that make sense? Should the advice be to not exceed 13A - not least because of the size of the plug's fuse?