Evening,
Carried out EV charger installation survey today & found this meter. Is that a 16mm concentric type cable adapter between cutout & meter?
This is a TT installation, tails unprotected. Not sure about installation method of DNO supply.
I'd like to upgrade tails to 25mm between cutout & meter, looks like the tails adapter can be removed & replaced with standard tails?
Also - meter is only rated for 80A, unsure of cutout fuse size.
Maybe easier to have smart meter fitted & convert to TNC-S