I have a 6mm main protective bonding conductor from a 1981 install; adiabatic equation says this is sufficient and no signs of thermal damage. (Discussed in separate thread).
Gas was not bonded, it's a big job to run new cable so I've used redundant water bonding as now all plastic to bond gas but need to join as too short. Is this allowed?
It's a TN-C-S
Michael I think as far as main bonding goes now 10mm is the minimum with TNCS especially with new work. But if the underground gas service to the property is actually plastic the internal pipework may not be extraneous and require bonding.
It's a TN-C-S
How are you intending to make the joint?
I need to check underground pipe, school boy error!
Does extending a cable to correct location count as new, or is this existing?
I know TN-C-S is treated different..............
I don't see how you can justify utilizing the redundant 6.0 for a new bond.
Bit more info on current install to help ascertain if should be treated as new or existing.
Current install bonded water, but was disconnected sometime ago when plumbing was upgraded to plastic. Previously as this pipe was also connected to boiler you could argue boiler was bonded (Sort of). Then all pipes looped at boiler. I'm putting join on water bonding here and extending to meter box.
Is the water pipe capable of introducing a voltage into the house? if it is then bond it. If it doesn't then test any copper pipework to see if is extraneous.
Off topic, previous EICR done after plumbing upgrade noted 10mm bonding and 16mm earth. He also ticked checked continuity of both. Beyond belief..........
If the gas has never been bonded and you are now going to put one in place it must comply with current standards, 6.0 does not satisfy this requirement.