Discuss Can you join Main Protective bonding conductor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I have a 6mm main protective bonding conductor from a 1981 install; adiabatic equation says this is sufficient and no signs of thermal damage. (Discussed in separate thread).
Gas was not bonded, it's a big job to run new cable so I've used redundant water bonding as now all plastic to bond gas but need to join as too short. Is this allowed?
It's a TN-C-S
Michael I think as far as main bonding goes now 10mm is the minimum with TNCS especially with new work. But if the underground gas service to the property is actually plastic the internal pipework may not be extraneous and require bonding.
It's a TN-C-S
How are you intending to make the joint?
I need to check underground pipe, school boy error!
Does extending a cable to correct location count as new, or is this existing?
I know TN-C-S is treated different..............
Bit more info on current install to help ascertain if should be treated as new or existing.
Current install bonded water, but was disconnected sometime ago when plumbing was upgraded to plastic. Previously as this pipe was also connected to boiler you could argue boiler was bonded (Sort of). Then all pipes looped at boiler. I'm putting join on water bonding here and extending to meter box.
Is the water pipe capable of introducing a voltage into the house? if it is then bond it. If it doesn't then test any copper pipework to see if is extraneous.
If the gas has never been bonded and you are now going to put one in place it must comply with current standards, 6.0 does not satisfy this requirement.
Why are you extending to meter box? Perfectly fine to bond at 1st accessible point into building. If your extending that then you are altering it therefore needs to be 10mm all the way to the MET imo.
I chuckled at your comment "pipework was UPGRADED to plastic" not sure plastic can be considered an upgrade rather than good old solid copper.
How have you performed an adiabatic calculation on a cable which isn't there to disconnect any protective device? Main protective bonding is not sized based on adiabatic calculations.
I think that's the case, it's a bit like if you ran a spur from an older RFC, you wouldn't use 2.5 with the old 1mm CPC, generally any new work which includes alterations or additions must comply with current standards.
Reply to Can you join Main Protective bonding conductor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
6K
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...
Hi all, just looking for guidance on how you would code a 2.5mm main earthing conductor on a property with 10mm line conductor. Basically on a...