I am pricing a job to wire 21 new pitches for a caravan park. There will be a meter box beside each caravan with a 16a trip. I will split it into the 3 phases, so 7 caravans per phase.

Im just trying to figure out how to calculate the cable size. Is it better to run a ring main to pick up 7 caravans? If so how do I do a cable size calculation for ring main?

Cheers
 
a 10.0mm SWA radial for 7 pitches will be adequate . probably even a 6.0mm, considering diversity.
 
You could do anything from installing a feeder pillar centrally with a seperate radial to each pitch up to running a large 3 phase cable with a Y joint to tap off a phase for each pitch.

The physical layout of the site and distances involved may have an influence on what the most economical way is.
 

Reply to Caravan site, cable size in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock