I'd also be binning the two of the three RCDs wired in series to each caravan! The one at the mains intake and the one at the DB adjacent to the caravan! If a TT system then a type-s could be needed at the mains intake position.
Depending on the max demand at each caravan I'd be looking to feed the SWA into a two way IP rated enclosure directly adjacent to the unit with a 100A main switch and a 32/40A type b feeding a 63A commando socket.
so then why the 100A imcomer?
80 A will cut it Damian....it may be cheaper...or the same price for either...