Guys/gals, in a domestic install of smoke/heat detectors, beyond issuing an EIC or Minor Works, do any of you also issue any other form of "fire alarm" certification? If yes, what do you issue?
Many thanks.
I use domestic fire certs from SELECT. PM me your email address and I'll see if I can email you the PDF
Yes, fire alarm installation certificates
I use the ones from the software package I use.
But before that I used the carbon copy type ones on pads from the wholesaler
For a domestic certification to BS 5839-6 is required.
Reactions: 1 person
Thanks all for the responses. I've been using the NIC online forms, but got into a debate with another electrician who was adamant that in a domestic LD2 system, nothing beyond the electrical Certs was required........although maybe Murdoch agrees with him???
Reactions: 1 person
My LABC expects to see fire certification in domestics. But weirdly they don't give a rats monkeys who wired up the house!
Reactions: 1 person
I was discussing smokes with my Stroma assessor recently - we agreed that they don't come under the remit of the schemes, or even sparks as they are not in BS 7671
Not sure what Stroma have to do with it.
But your fire alarm should be designed, installed and tested to BS 5839 and yes BS 5839 also makes reference to BS 7671 as well as building control part B vol 1 in this case.
Only the same as your emergency lighting should be to BS 5266
Reactions: 1 person
If a sparks installs them then they must be under the remit of that sparks, and they should be complying with the current British standards.
Sent from my iPad using Tapatalk