So I went to the job today and had a better look around as the kitchen had closed.

The unit is has a 63 amp supply. Told the client I couldn't wire the cooker (15kw) as this
would put here well over 80amps, well I got a mouthful of abuse from her about how
much she had paid for this oven, and how she will find a "better" electrician to wire
this for her lol.

Did I do the right thing not wiring this?

How would you handle a client like this?

So the appliance has a full rated current of 67A, connections rated at 40A, with diversity applied requires a circuit capable of 27A, yet can't be connected because it requires a 63A supply ?
 
So I went to the job today and had a better look around as the kitchen had closed.

The unit is has a 63 amp supply. Told the client I couldn't wire the cooker (15kw) as this
would put here well over 80amps, well I got a mouthful of abuse from her about how
much she had paid for this oven, and how she will find a "better" electrician to wire
this for her lol.

Did I do the right thing not wiring this?

How would you handle a client like this?
Design the circuit for the load calculated , install as per instruction and charge accordingly
When the incoming fuse pops , tell her I told you so .....
 
Obviously diversity can still be applied but the sum given in the OSG is for a domestic cooker.
 
So I went to the job today and had a better look around as the kitchen had closed.

The unit is has a 63 amp supply. Told the client I couldn't wire the cooker (15kw) as this
would put here well over 80amps, well I got a mouthful of abuse from her about how
much she had paid for this oven, and how she will find a "better" electrician to wire
this for her lol.

Did I do the right thing not wiring this?

How would you handle a client like this?

I'm a little bit lost here, what unit has a 63A supply? I thought this was a commercial kitchen?

What is the existing maximum demand?
 
Last edited by a moderator:
I'm a little bit lost here, what unit has a 63A supply? I thought this was a commercial kitchen?

What is the existing maximum demand?
Yes me too not a little bit lost though completely bloody confused. First you are looking at providing a supply now you are talking about an existing supply????? What do you mean by "unit" exactly?
 