A combi boiler is wired into a plug, which is plugged into a single socket. The Nest receiver, controlling the heating (heat link I think they call it), is wired into a separate plug, which is plugged into a socket on another circuit.

So 2 circuits interlinked, a minimum C2.

However, could this also create a 'widowmaker', where unplugging either of the plugs, while the other is still energised, would leave the pins live?
 
It is only a problem if the supply from the heat link is looped to the relay in the heat link.

if the heat link supply is only used to power the unit and the boiler is connected Only to the volt free contacts (relay) then it is not a danger.
however a sticker to remind service people to isolate at both supply’s would be a good addition.
 
It is only a problem if the supply from the heat link is looped to the relay in the heat link.

if the heat link supply is only used to power the unit and the boiler is connected Only to the volt free contacts (relay) then it is not a danger.
however a sticker to remind service people to isolate at both supply’s would be a good addition.
Thanks @James . Looking closely at the wiring diagram, I see what you mean now. Possibly no code. I'll have to go back for a closer look.
 
Isn’t there something in the manual that says it all needs to be isolated from one point?

How difficult would it be to rewire the receiver into the wiring centre?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Warwickshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Combi boiler wiring - C1 or C2?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Thread Tags

Advert

Thread statistics

Created
Pretty Mouth,
Last reply from
Pretty Mouth,
Replies
5
Views
1,877

Advert

Back
Top