After some advice please...

I visited a property today to cost up a job. I spotted that the Main earth (16mm) had been bared back on its way to the board and clamped to the gas pipe. (Doubling up as a bonding conductor). The cable was continuous and was not cut or joined. Any installations I have ever done have been separate bonding and earthing conductors back to the MET. Is this a best practice today or does it actually say in a specific regulation that it does need to be separate (I've looked {probably not very well} but can't find anything) or is doubling up an old practice I've been missing for saving the pennys for my Friday beer money??? (still learning :wink5: ).

I can see its doing the same job but want to make sure any advisories to current regulations I give the customer are correct.

Cheers
 
Combined bonding and earthing conductors are permitted, but the connections should be to the MET.
As Sintra says you do need to be able to disconnect the earthing conductor to test Ze, so if this conductor is not removable at the supply head end then you would need to remove both the earthing conductor at the main board and disconnect the bond to the gas.
 
Thanks guys - yes, you can disconnect the gas bond at the clamp and/or the earthing conductor from the head to get a clean Ze.

Appreciate the feedback on the combined and clearing that up........
 
I would say that is not acceptable as it would be a little tricky to do a Ze.
hows that then?..
just disconnect the conductor from the bonding clamp/s....for the duration of the test

sorry....just noticed #4
 
Not exactly good practise though is it. Come on the main earthing conductor should go directly to the met.
 
Combined Main Earth & Gas Bonding

Doesn't seem any more effort to do it in the traditional fashion in the first place
 
My gut tell me not good, will still work of course but seems a bit lazy. Never seen that, good post!
 