Commercial periodic with loads of IT kit. One or two of the disboards have 4 pole isolators/main switches. I believe switching the neutral in some cases is incorrect and potentially dangerous.

When should you NOT switch the neutral conductor??

Thanks in advance for any info.
 
Hi There,

BS7671:2008 regulation 537.2.1.1 states that "Every circuit shall be capable of being isolated from each of the live supply conductors. In a TN-s or a TN-C-S system, it is not necessary to isolate or switch the neutral conductor where it is regarded as being reliably connected to Earth by a suitably low impedance."

I have never come across a situation where disconnecting the neutral is dangerous. In fact it's a bonus if you can, less risk of picking up a back feed through the neutral conductor for total isolation. Although according to the reg's not essential.

Cheers

Glenn
 
Not a fused neutral - this is 4 pole incomers on the 3 phase disboards. My inspecting engineer thinks there may be a problem with switching a neutral/PEN conductor in this scenario.

I don't see a problem - hence the post !
 
Don`t see a problem either.

If 537.2.1.1 does state that (unable to check at this mo) then as the Neutral is now considered a LIVE conductor...

Hope it helps
 

Reply to Commercial periodic question in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
436
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed...
Replies
1
Views
1K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock