Commercial periodic with loads of IT kit. One or two of the disboards have 4 pole isolators/main switches. I believe switching the neutral in some cases is incorrect and potentially dangerous.
When should you NOT switch the neutral conductor??
Thanks in advance for any info.
Hi There,
BS7671:2008 regulation 537.2.1.1 states that "Every circuit shall be capable of being isolated from each of the live supply conductors. In a TN-s or a TN-C-S system, it is not necessary to isolate or switch the neutral conductor where it is regarded as being reliably connected to Earth by a suitably low impedance."
I have never come across a situation where disconnecting the neutral is dangerous. In fact it's a bonus if you can, less risk of picking up a back feed through the neutral conductor for total isolation. Although according to the reg's not essential.
Cheers
Glenn
Not a fused neutral - this is 4 pole incomers on the 3 phase disboards. My inspecting engineer thinks there may be a problem with switching a neutral/PEN conductor in this scenario.
I don't see a problem - hence the post !
Don`t see a problem either.
If 537.2.1.1 does state that (unable to check at this mo) then as the Neutral is now considered a LIVE conductor...
Hope it helps
Reply to Commercial periodic question in the Australia area at ElectriciansForums.net
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Deleted member 155212
This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...