Discuss Connection issue with swa in the UK Electrical Forum area at ElectriciansForums.net
I need to run an out door supply.
However the dist board is boxed in.
There is access back entry but that doesn't help glanding a swa.
Could you gland outside to a through box them carry the same cable to the breaker?
Taking an earth leas from the conduit box also.
Yes you can.
Well the conduit box will be behind some boxing in and under a lean to
I would leave the box accessible. Not behind some boxing in.
Also the cable from the box to the breaker will have to be RCD protected, depending on installation method.
I was going to put it on a 32 amp rcbo
As it's going to an outdoor isolator for a hot tub.
What size cable do you intend to run, how far is the hot tub from the C/U, what loading is the hot tub, what installation method are you intending to use.?
why do some people think we can do a job for them while on this forum .
take picture of the work it will tell a story.
Not to be rude but how is a picture of a wall where I intend to mount a conduit box going to help ?
I'm not at the job right now.
Just wanted to confirm I can gland somewhere else other than at the ccu since its not something I've done ever.
This forum always starts off helpful then soon turns to negativity and do you want me to do the job for you.
So helpful, probably get more help on a fitters forum.
take no noticeof buzzlightyear. (nobody else does :)). your plan saounds OK. gland SWA into a adaptable box, carry the tails into the CU ( in pvc tube is a good idea ), add an earth tail for earthing the armour, job's sound.
we all need help for time to time. but when you plan a job or start you have to become a engineer has well has a spark .put a plan on a plain paper let the dog see the rabbit .
to help you
to help you.
Depending on the fixed load a 2.5mm off a 32amp mcb is no different than spurring off the ring final directly from the Mcb at the consumer unit.
If overload protection isn't required then all the 2.5mm needs is fault protection which the mcb will give.
I personally would size the mcb so Ib<In<Iz but it wouldn't necessarily be a non compliance
Think he's planning a radial buzz , just off a 32 amp mcb.
I'd go 20amp but just saying that what he proposed isn't necessarily non compliant.
Why you would use a 32A device on a 2.5 cable to supply a 13A, which I assume to be a socket, is beyond me.
if his SWA tails come straight through the wall, not buried <2" in plaster, no need for RCD protection unless it's TT.
Ok in that case a 16a MCB. But if it's going straight to an external rotary isolator you'd need the RCD protection at source for the tub.
It is different to a 2.5mm spur from a ring, this is a dedicated circuit to a single appliance and the spur from a ring is one point out of a number of points for general use. The ring circuit relies on loads being spread around the circuit to work correctly and it is advised that fixed loads greater than 2kW aren't fed via a ring circuit.
Yes you could prove by calculation that the mcb will provide fault protection for the cable, but this seems like an over the top and unnecessary thing to do for a domestic installation. Especially when you can guarantee that anyone who looks at this installation in the future will label you as a cowboy for having done it that way.
Far simpler to install an ocpd which is better matched to the load.
I hope you do realise that I'm not suggesting that it's spurred from the ring circuit, more suggested that if it was supplied from a 32 amp mcb on its own dedicated radial then as it's a fixed load it not necessarily no compliant as people are suggesting.
As stated I wouldn't use a 32 amp on a 2.5 , mearly suggesting it's no different being protected by a 32 amp as a spur is directly from the consumer unit when overload isn't a factor.
And yes the mcb will protect against fault protection you don't need a calculation to work that out.
Even a generic I2t let through value from a manufacturer will tell you that for a disconnection time under 0.1 of a second
does manufacturer say a 32A RCBO or a 32A circuit? what's the wattage rating of the tub?
thing is... if the tub is rated @ 13A, why in hell is a 32A OCPD called for. only needs a 16A or 20A, then 2.5mm cable will comply in all ways.
Reply to Connection issue with swa in the UK Electrical Forum area at ElectriciansForums.net
For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
7K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...