Been trying to work out the earthing conductor size using the adiabiatic equation for over an hour and totally lost myself. (Wouldn't think I got a GCSE A for maths) lol

The OSG without calculation shows that the minimum earthing conductor is 16mm with 10mm for protective bonding.

However, I have seen an example equation on the tlc website which is almost identical and it works out that 6mm is sufficient as the earthing conductor.

I believe that 10mm for earthing conductor and 10mm for protective bonding is suitable.

Does anyone have any useful guides for learning and working out the equation?

Also, does anyone agree that 10mm is sufficient for earthing conductor and bonding (even if the main fuse was 100a)?

Thanks
 
Also, when working out r1 + r2 you need the length of the run. If I'm trying to work out the earthing conductor size, would I just use 5 metres which is the length of the tails?
 
The minimum csa of main earth are in table 4.4 of the osg it shows you that for a main live and neutral conductor sized at 16mm the minimum main earth should be 16mm and main bonding should be 10mm obviously the adiabatic equasion would come out significantly lower but if you are upgrading the board then you should make sure it complys with the current regs and the regs state 16mm main earth and 10mm bonding so I would just use 16mm main earth its not gonna cost much more.
I think it says some where in the regs not sure where that a live conductor 16mm or less should have the same size earth as the live which is wierd as twin and earth have different size live and cpc
 
I have also read the sane information.

However, I already have 10mm cable lying around and as its for a relative then I won't charge them. Would need to purchase 16mm earth.

Does it not say that either use the table or calculate it?
 