It's been against the regs for at least 35 years, probably longer. And whether it complied or not, it's as dangerous now as it was then.
The problem arises when some poor sod comes along to change, for example, a ceiling rose.
With the MCB off/fuse removed on the circuit being working on, and the circuit proved dead work proceeds.
If there is a load on the other circuit (the one that is sharing the neutral) full line voltage will appear on the neutral as it is pulled from is terminal. It's f***ing dangerous (to electricians, handymen, diyers and anyone else likely to work on it) because safe isolation requires two (or more) MCBs to be turned off.
Under normal circumstances it does not pose any problem to the installation user.
that's why you should knock the main switch off.
that's why you should knock the main switch off.
that's why you should knock the main switch off.
If I'd done that on the last borrowed neutral if found then if have shut down a six screen cinema complex and part of a shopping centre, I don't think it would have been acceptable!
It's been against the regs for at least 35 years, probably longer. And whether it complied or not, it's as dangerous now as it was then.
The problem arises when some poor sod comes along to change, for example, a ceiling rose.
With the MCB off/fuse removed on the circuit being working on, and the circuit proved dead work proceeds.
If there is a load on the other circuit (the one that is sharing the neutral) full line voltage will appear on the neutral as it is pulled from is terminal. It's f***ing dangerous (to electricians, handymen, diyers and anyone else likely to work on it) because safe isolation requires two (or more) MCBs to be turned off.
Under normal circumstances it does not pose any problem to the installation user.
A competent experienced electrician who falls for this old chestnut would get a slap from me for being a ****.
If they weren't both on the same neutral bar surely you'd have both RCDs tripping constantly anyway ?
How exactly are you going to include borrowed neutrals in your safe isolation procedure? You isolate and lock off the submain feeding the board you are working on, so all fine and dandy. You remove the board, fit the new one and start connecting up. Somebody switches a lightswitch in another part of the building which operates a light with the neutral borrowed from one of the circuits in the board you are replacing.
Unless you are operating full live working procedures then you don't stand a chance against it.