Apologies for not providing more info.

Have no fear, I am certainly not a cowboy when it comes to electricity!

In fact, I'm only just into my second year studying to be a domestic electrical installer, then planning on moving up to commercial/industrial.

I'm asking this as after having attended my first practical week, there was some discussion about the correct order that switches in the CU should be wired in.

In my understanding, the feed from the supply comes in to the main switch, and then to the circuit breakers for each circuit in the installation, yes?

Some folk attending were questioning if there should be an initial circuit breaker before the individual ones controlling the circuits.

I just thought I'd throw the question out there...
JW usually has a good explanation on all thing electrical
 
Sorry Murdoch, my post mentioned Main Switch to isolate the rest of the circuits connected to this fuse board, 1 fuse board 1 main switch, no mention of another fuse board, if the installation had more than 1 fuse board then the same would apply to each fuse board, can't see how you corrected it for me.
See what you are getting at now Murdoch, ignore my post above
 
Inside a CU the main switch is first, then (if present) DP RCDs protecting a block of circuits, then MCBs or RCBOs protecting individual circuits or distribution circuits out of the CU.
If there are multiple boards fed directly from the same supply then there should be a main switch that isolates the installation as a whole between the supply and the boards, though each board should have its own main switch as well.
If the supply is remote from the board (generally >3m) then a circuit protective device should be installed less than 3m from the supply head.

Supply and Isolators main switches.jpg
 
Gary
Hi you don't tell us what you are in your profile, by that I mean: Electrician, Domestic Installer, Apprentice, Trainee or DIYer in order to tailor replies we need to know at what level you are.
It's difficult to respond to a O.P. in the way of terminology if people don't fill it in.
 