I have to jump onboard this one too,im doing a cu change tommorrow,had a look last week,nothing labelled,decided to do a PIR first,main bonding needs upgrading(nightmare run)20 mtrs,one thing i found was that the upstairs/downstairs lighting was on one cable,probably a junction box under floor upstairs,now i know that if it goes on 1 CB then it does not conform with the regs as up/down would both go if a fault arised,so unless she wanted me to find the JB and run a new feed to deivide into 2 circuits is it reasonable to put down on the EIC deviation?,I can offer the idea but i cant force it upon them.what do you guys think
You're not installing this circuit, you're simply dealing with it. You can't change a board in a house and at the same time include making the house into a textbook installation.
Strangely enough I like hotch potch houses where you can add a socket in a bedroom thats spurred onto the kitchen ring, and a light in the fusebox cupboard thats all surface mounted and not needing an RCD.... actaully helps with the nuisance aspect. But we're not taught to do it this way are , no, "Up lights", "down lights", "up sockets", down sockets"..... and so on.
As long as there is a detailed, laminated, firmly affixed legend so its clear whats what by the board ....