I am having a problem understanding a question in mylearning book.

It gives the scenario:

The following 6 line to earth values were recorded in aninstallation. What would be the expected values at the origin and what actionsshould be taken, if any.

Circuit 1 = 25 Ω
Circuit 2 = 2 Ω
Circuit 3 = 10 Ω
Circuit 4 = 20 Ω
Circuit 5 = 25 Ω
Circuit 6 = 15 Ω

So I’m assuming this is a continuity reading as it doesn’t state.

What would be the steps to figure this out. I’m not askingfor the answers because I need to understand and work it out myself, however I can’tunderstand where I’d start. Add them all up and divided by 6 to get andaverage?

Any help would be appreciated

 
I am having a problem understanding a question in mylearning book.

It gives the scenario:

The following 6 line to earth values were recorded in aninstallation. What would be the expected values at the origin and what actionsshould be taken, if any.

Circuit 1 = 25 Ω
Circuit 2 = 2 Ω
Circuit 3 = 10 Ω
Circuit 4 = 20 Ω
Circuit 5 = 25 Ω
Circuit 6 = 15 Ω

So I’m assuming this is a continuity reading as it doesn’t state.

What would be the steps to figure this out. I’m not askingfor the answers because I need to understand and work it out myself, however I can’tunderstand where I’d start. Add them all up and divided by 6 to get andaverage?

Any help would be appreciated

misread it.

have a look in your onsite guide and check if the values comply,

remember that zs= ze+(r1+r2)

what do you think?

Sent from my SM-G900F using Tapatalk
 
Last edited:
This question would make a lot more sense if the values were in MOhms, and the question was relating to being able to perform a resistance in parallel calculation, and illustrating the difference between single circuit and global IR testing.

It is very poorly worded though.
 
This question would make a lot more sense if the values were in MOhms, and the question was relating to being able to perform a resistance in parallel calculation, and illustrating the difference between single circuit and global IR testing.

It is very poorly worded though.

I agree. Hence why im confused. At the top of the page it says im on the section of "insulation resistance" but that confuses me even more
 
i would imagine that it should be an IR question and the figures should be in Megohms. then you would work out the resistance of the circuits in parallel to give a global value at the origin. ( using 1/Rt = 1/R1+1/R2+1/R3.......)
 
i would imagine that it should be an IR question and the figures should be in Megohms. then you would work out the resistance of the circuits in parallel to give a global value at the origin. ( using 1/Rt = 1/R1+1/R2+1/R3.......)

:-/ sorry yes it does

my mistake. Note to self, read carefully!
 
Doing some research on the calculations because it's new to me.

would this be correct with the values I have.

1/R1+1/R2+1/R3+1/R4+1/R5+1/R6

=

1/25+1/5+1/10+1/20+1/25+1/15

=

0.04+0.2+0.1+0.5+0.04+0.066

=

1/0.496 = 2.016 overall value
 
Doing some research on the calculations because it's new to me.

would this be correct with the values I have.

1/R1+1/R2+1/R3+1/R4+1/R5+1/R6

=

1/25+1/5+1/10+1/20+1/25+1/15

=

0.04+0.2+0.1+0.5+0.04+0.066

=

1/0.496 = 2.016 overall value

I get 2.014 (reciprocals not rounded) so you are correct. The only thing I noticed was that in your initial post circuit 2 is listed as a value of 2, and in your final calc it is 5.

You say you have not performed this calc before ? why are you been given questions on subject matter you have not yet covered ?
 
I get 2.014 (reciprocals not rounded) so you are correct. The only thing I noticed was that in your initial post circuit 2 is listed as a value of 2, and in your final calc it is 5.

You say you have not performed this calc before ? why are you been given questions on subject matter you have not yet covered ?


They will surely have covered resistors in parallel previously to this i would of thought. :smile:
 
andy, i don't think it's a question of him not having done the calcs., but more that he needed to know what the question wanted.
 
Well I covered insulation resistance testing in one of books but I don't remember having to use that formula. I'll have to recap

Andy, well spotted. It should have been a 5 in my original post
 
Just a reminder that the final figure will always be lower than your lowest original value when doing parallel calcs like this - just a quick way to check and make sure you haven't gone obviously wrong somewhere.
 
thanks everyone for the help

So, I’m supposed to say what action should be taken if any.

Apart from the obvious safety precautions and use of correcttester and correct voltage I cant think of anything else to add.

The reading seem ok?? they are quite varied but I think that’snormal within different circuits

They are all above 1megaohm
 
thanks everyone for the help

So, I’m supposed to say what action should be taken if any.

Apart from the obvious safety precautions and use of correcttester and correct voltage I cant think of anything else to add.

The reading seem ok?? they are quite varied but I think that’snormal within different circuits

They are all above 1megaohm

I think personally, although the guidance states anything less than 2ohms should be investigated, I'd probably investigate a reading as low as this.
 
I think personally, although the guidance states anything less than 2ohms should be investigated, I'd probably investigate a reading as low as this.

TUT TUT, HT, you left the Meg out. :tank:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
-
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
continuity clarification
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
22

Thread Tags

Tags Tags
continuity

Advert

Thread statistics

Created
gazdkw82,
Last reply from
hightower,
Replies
22
Views
2,505

Advert

Back
Top