Very, have you nulled your leads first?

Sounds like you have the resistance of your test leads plus the resistance of the 10mm cable in your reading .
 
parrallel paths would reduce the reading anyway. try a bigger screwdriver on the conns.
 
Hey, got it sorted. The batts were goin' flat in the Megger and I hadn't disconnected it from the earth clamp! Cheers anyway.
 
If the cable is left connected to the clamp on your water supply and disconnected from the earth bar in the CU, how would a parellell path come into it anyway?

If a bonding cable is checked end to end with both ends being bare copper, then when its connected to the bonding clamp and the bonding clamp has a poor connection, then the resistance could be stupidly high, couldn't it?
 
Which is why I will always do a second test once the cable has been terminated as I like to be certain the pipes themselves are connected as intended to the MEB
 

Reply to Continuity Of Water Service Earth... in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock