Hi folks, i have a 16 way British General CU which was configured as split load.

I'm converting to all RCBOs which is fine apart from one small detail, i don't have a single neutral bar long enough.

The earth bar is fine - plenty of ways for CPC doubled with RCBO functional earth.
The neutral bars are 9 way and 8 way - i need a 17 way (minimum) single piece.

Can't for the life of me find them for sale anywhere! Does anyone know where i can get one?
Alternatively, can the 2 separate neutral bars be linked with one of the existing 25mm cables?
(Although i'd really rather not do this - seems like a hack and is not clear at a glance what is going on)
Any help greatly appreciated.
 
If it is split load as I know it then some are protected by a single rcd with the others having no rcd, correct?
 
just link the N bars. that's how CUs used to be configured and you took the link out if you wanted 2 RCDs. a "U" shaped bit of bare copper link was fitted by manufacturer.
 
Might be cheaper too replace the whole unit ...... Wonder why this is being considered and how old the board is?
 
just bodgit and scarper in line with niceic guidance. ( as long as your subs.is not overdue).
 
just bodgit and scarper in line with niceic guidance. ( as long as your subs.is not overdue).
Or Stroma, NAPIT et al. Bit harsh tel. Not all us NIC guys are cowboys. At least north of the boarder we only have 2 registration bodies and no DI's :)
 
Thanks very much for the replies.
Regarding the 3 switches, i can't get away with that as it would take up too many ways which is one of the reasons for switching to RCBOs in the first place.

I don't have a manufactured link cable or solid link for connecting 2 separate neutral bars, but i could crimp one up. It just seems like a bit of an untidy job to me when i know the terminal bars can be had from somewhere. Interestingly, you can actually buy the exact same CU as a main switch only board which has the single piece terminal bar. Obviously i'm not going to go out and buy a whole new CU though.
 
I don't have a manufactured link cable or solid link for connecting 2 separate neutral bars, but i could crimp one up.
That's your option. But you'll need to carefully know how thick that neutral link is going to be. It could be carrying a lorra current.

As in your first post. Just use the neutral cable from the old RCD to link the two neutral bars.

But why do you simply not just put two RCBO neutral tails into each of the existing neutral busbar holes??? Numbering will not really matter as the circuit line and neutrals will be terminated on the RCBO itself.
 