Hi,he

What is the correct application of diversity, when a separate hob and oven share a single feed. As far as I see it, electrically they are the same as a free standing cooker - or does a cooker have a limiting mechanism to prevent all circuits from working at the same time.

Hob is 6.7kw, and oven 4.6kw. This would be approx 49amps.

If diversity is applied individually a 29 amp circuit would be ok. If diversity applied on the joint load, then it is down to 22amp. Which is the correct method?

In any case, 6mm (clipped), with a 32a breaker should feed both without a problem, and also follows OSG recommendation of 32 amp for 15kw max.
 
should not be a problem.
 
Apart from using a dual connection plate (scolmore), what is the best way to wire two units to a single feed?
 
you can get 3 x 6mm cables into a single CCU., but a dual CCU would be better.
 
dunno about diversing, but i've divorced 2 cookers.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Correct application of diversity, separate hob/oven on single feed.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
jase31,
Last reply from
telectrix,
Replies
6
Views
5,124

Advert

Back
Top