Deleted member 26818
Of course, if the Gas and Water are supplied in plastic, there would be no need for a separate Earth conductor.
you can't run plastic gas pipes in a building as it would be catastrophic in a fire. If the gas is run in plastic externaly it has to change to be being metallic before it enters the building. The yellow plastic pipe feeding external gas meters is not allowed to be exposed so again needs to change to be being metallic before it comes out of the ground.....in other words it's pretty hard to get away with not bonding gas.Of course, if the Gas and Water are supplied in plastic, there would be no need for a separate Earth conductor.
I wish I’d taken a bit more time in my reply, but that is exactly what I did! Thank you for the perfect explanationThis will come under what's called a Building network operator installation. The DNO will give you guidance on what they want but a single point of isolation for the building will be needed and a ryefield board or similar so it can be sealed. Normal layout is head, fused switch or isolator depending on the distance, ryefield, Meter, switch fuse or isolator them armoured cable to the flat. You have to get it all in place leaving the connection ready for the DNO to connect in to the head and have the tails in place from the ryefield to the meter and from the meter to the switch fuse/isolator ready for the meter operator to connect.
Would you need a switch fuse after the BEMCO or ryefield as you call it? or just from the BEMCO via meter and double pole isolator as you would have potential say 2 60 amp fuses in series and it’s a different set up to say a house where the tails are greater than 3 meters and is the origin of the supply?This will come under what's called a Building network operator installation. The DNO will give you guidance on what they want but a single point of isolation for the building will be needed and a ryefield board or similar so it can be sealed. Normal layout is head, fused switch or isolator depending on the distance, ryefield, Meter, switch fuse or isolator them armoured cable to the flat. You have to get it all in place leaving the connection ready for the DNO to connect in to the head and have the tails in place from the ryefield to the meter and from the meter to the switch fuse/isolator ready for the meter operator to connect.
Hmm, seen quite a few yellow plastic pipes connected to internal meters. Have even seen them bonded.you can't run plastic gas pipes in a building as it would be catastrophic in a fire. If the gas is run in plastic externaly it has to change to be being metallic before it enters the building. The yellow plastic pipe feeding external gas meters is not allowed to be exposed so again needs to change to be being metallic before it comes out of the ground.....in other words it's pretty hard to get away with not bonding gas.
Like I say I’m not a gas engineer but I’ve never seen plastic gas pipes enter a building from the outsideDoesn’t have to be copper where it enters a building.
Tell you the truth Ian we just install switch fuses but reading the info the DNO supply you with, you could use a DP switch as you have the fuse in the Ryefield/BEMCO board. 9/10 times the flats we do a 60A supply is adequate so 100A fuses in Ryefield and 60A fuses in the switch fuses. Using the rule of thumb of x 1.6 for discrimination between upstream and downstream fuses of the same type then discrimination is just about achieved. I prefer it this way if it's possible so if there was a fault, the fuse in the switch fuse goes and an electrician can replace it rather than entering a sealed Ryefield which is frowned upon by whoever sealed it.Would you need a switch fuse after the BEMCO or ryefield as you call it or just from that via meter and double pole isolator as you would have potential say 2 60 amp fuses in series and it’s a different set up to say a house where the tails are greater than 3 meters?
That’s a good way of looking at it lee.Tell you the truth Ian we just install switch fuses but reading the info the DNO supply you with, you could use a DP switch as you have the fuse in the Ryefield/BEMCO board. 9/10 times the flats we do a 60A supply is adequate so 100A fuses in Ryefield and 60A fuses in the switch fuses. Using the rule of thumb of x 1.6 for discrimination between upstream and downstream fuses of the same type the discrimination is just about achieved. I prefer it this way if it's possible so if there was a fault, the fuse in the switch fuse goes and an electrician can replace it rather than entering a sealed Ryefield.