Discuss CPC for shower! in the Australia area at ElectriciansForums.net
Hi guys, i just changed a 8.5kw electrical shower for a friend, the live is 6mm2 and i believe it is fine, the only thing is the cpc, looks like 1.0mm, at most 1.5mm, i checked codes, but still not sure about it, is this cpc ok?
cheers
cheers
First response to a post for me. Assuming both protective and line conductors are copper, then according to table 54.7 in regs (pg 130 in mine), suggests csa of protective conductor should be (at least) same as line conductor?
Thats the way I'm reading it anyway, but have to admit I've never seen a 6mm cable with a 6mm earth? Having said that, if you can imagine nearly 40amps running down your skimpy cpc in a fault condition then it doesn't sound ideal to me!
Pat
Use the adiabatic equation.
Hi,
Whats the length of the cable and how is it run ( under floorboards, clipped direct etc ).
You said its old cable, is it the old colours Red, Black ??
You also mentioned 8.5kw shower, so that equates to 36.95 amps ( ib ), so depending on your fuseboard, you need at least a 40amp mcb.
So work out your current -carrying capacities, volt drop and adiabatic to get correct cable selection. You should really know what size cable you have selected, as this can have a big effect when the shower is on ( over heating the cable etc ).
Hope this helps,
Sav
Hi,
Hope this helps,
Sav
i only changed the shower and did not touch anything else. the colors are old: read and black. 6mm.
i could find easily the minimum size of main bonding conductor is 10mm, but just cannot find minimum requirement for cpc in the bs7671, is 1.5mm really ok?
i have not done the adiabatic equation, but guessing as some of the results i got previously from using that equation, they maybe , yes .
BUT, you must make sure you do it properly i.e supply protective device etc.....
Sav
Reply to CPC for shower! in the Australia area at ElectriciansForums.net
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...