Discuss CPC missing on ring final in the UK Electrical Forum area at ElectriciansForums.net
Morning All,
Currently carrying out an EICR and going through ring final steps with the following readings:
r1: 0.31ohm
rn: 0.32ohm
r2: 0.03ohm
Started taking sockets faces off to find that there is no cpc, only fly lead to metal patress box and steel conduit trunking. (See photo)
When i carry out R1+R2 i get a reading of 0.48ohm.
I suspect I'm picking up parallel paths for R1&R2 reading.
Question is what do i code this on report and any recommendations on remedial?
Thanks in advance
Erm, what do you mean no CPC? Surely the low R2 readings are your confirmation that the CPC is actually rather good, as steel conduit usually is. Do you have concerns about the integrity of the conduit installation?
I expect the metal conduit is the CPC. You need to test the continuity of the conduit to the MET and get a satisfactory reading (although I'm guessing this is your R1+R2 that you already have, what did you actually test between to get this result?). Metal conduit used as the CPC is fine as long as it has continuity. Personally I have never come across it, others with more experience may offer extended advice to what I have written.
[automerge]1596449686[/automerge]
Does the (r1+r2) / 4 = (approx) R1 + R2 still apply to a ring which partly has metal conduit used as the CPC Lucien? I can't see the above formula working out though as the CPC will not be a ring.
In the OP's post (r1+r2) / 4 < R1 + R2 by a large amount. In fact the r2 is incredibly low, this implies the earth of the twin and earth has continuity shortly after leaving the CU??
Ps.. You reminded me of @Murdoch when you started your post, he always started 'Hmmm' :D
The CPC of a ring final is required to be in the form of a ring except where provided by metallic containment, in which case no particular configuration is specified and the crossed ends test is applied to L & N only. If the conduit is sound, it will invariably provide a much lower R2 than a CPC within a cable and the testing merely needs to confirm that it is within limits. The inspection should include a visual and tightness check of an appropriate sample of conduit joints.
How are you carrying out an R1+R2 test with steel conduit used as the CPC of a ring?
You aren't picking up parallel paths, you are picking up the CPC.
So far there is nothing to be coded on the report as you've not told us anything that suggests non-compliance.
Steel conduit is a suitable CPC so as long as it is correctly connected and passes testing it is fine.
Hi Lucien, The current installation of the ring final is a mixture of steel conduit (from the original installation), and 2.5mm T&E from an addition. I suspect they linked in to the original ring and then terminated at the DB in T&E, as all cables in the new DB are harmonised colours.
Hence when I carried out the ring final steps End to End and got the 0.03ohm's on CPC when r1 & rn were 0.31 & 0.32 respectively, I went on the hunt for the dodgy CPC and came across the original Ring final using the steel conduit as CPC!
I'm a little unsure of compliance in combining the methods in this manner?
I also came across a borrowed neutral to the Oven circuit (to who knows where, needs FI) which is tripping both RCCB's on the split board when trying to carry out Zs or even pushing the Test button! any advice on this one would also be appreciated!
[automerge]1596489781[/automerge]
Hi davesparks, please see my response to Lucien which answers your question on how I carried out the R1+R2 crossed, to get the avg 0.48ohm reading.
[automerge]1596489925[/automerge]
Hi Happyhippydad, many thanks for your comments, please see my response to Lucien which should clarify the situation.
Reply to CPC missing on ring final in the UK Electrical Forum area at ElectriciansForums.net
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...