Morning All,
Currently carrying out an EICR and going through ring final steps with the following readings:
r1: 0.31ohm
rn: 0.32ohm
r2: 0.03ohm
Started taking sockets faces off to find that there is no cpc, only fly lead to metal patress box and steel conduit trunking. (See photo)
When i carry out R1+R2 i get a reading of 0.48ohm.
I suspect I'm picking up parallel paths for R1&R2 reading.
Question is what do i code this on report and any recommendations on remedial?
Thanks in advance