I'm presuming you only need to add ferrules if you shorten the lead, or do you guys add them anyway?
They don't look like they have them, so guess they've been shortened.
Edit, op's replies just bee added.

I'm presuming you only need to add ferrules if you shorten the lead, or do you guys add them anyway?

show him reg. 526.9. ( from 17th . 18th. may be different number.).
.No that is the tub strap box used for fixing the SWANice job
Why is there a piece of cardboard wedged down the back of the consumer unit ? Packing to get level ?
Yes your right thanks for the adviceYou need to colour identify you bottom neutral
Can't be arsed with arguing, but where does that **** come from?![]()
17th Edition Amendment 3, 421.1.201 (ii)
states that consumer units shall be enclosed ...etc.
You can hardly call the CU enclosed if there's a gapping big hole in the back, especially as it's pointing at an easily combustable material such as wood.
The intent of that reg is to ensure the fire containment of the enclosure is maintained, which it isn't with a big hole in the back facing wood. It would be fine if it was mounted on a non-combustable wall, but it's not.
Think about it, what's the point of having metal enclosures, metal self closing doors over the mcbs, having to fit non combustable blanks, all designed to keep a fire within the CU, then a big hole that a fire can escape out the back of?
A couple of intumescent pillows stuffed in the holes will suffice.

It takes a real expert to do a messy install though ;o)))))Don’t fret, neatness comes with experience![]()
Does look good, be prepared to be ripped apart though![]()