Believe it or not Knob and Tube wiring is still OK in some US states!
View attachment 12480
View attachment 12480
Believe it or not Knob and Tube wiring is still OK in some US states!
View attachment 12480
Although i doubt O/P will have any issues here; try not to give the impression that fitting energy saving lamps will give the circuit design current more lee-way, the circuit should always be calculated with the max rated lamp that can be fitted to the outlet, additional to this a 1.8 factor needs to be applied to inductive lamps, and in the O/P's favour diversity can be applied when working out demand on the circuit too.Dont forget the BS7671 is not law! It is advised - you should follow it as much as possible unless you have a good reason not to - customer would not pay for a rewire is an ok reason
Do an Ohms law if your in doubt:
P=IxV
I=P/V
= 1000/230
=4.35A
Use a 6A MCB and you have more than enough room to move with.
If in doubt change all the bulbs to Energy Saving - you would only get a max of 140w (based on 10 lights at 14w Energy Saving Bulbs - 0.6A
Nobody would put the lights all on one circuit on a new system, but neither would they try and get money out of someone to change an existing system just because the cu was being changed. My thoughts anyway. Daz
I priced a C/U change in a 1 bed flat with only 4 circuits (1 lighting) I phoned elecsa and they reckoned it was perfectly satisfactory to put in a single RCD board. I quoted £230 for this. The guys jaw nearly hit the floor, another firm had come in and quoted £750.
Another very happy customer.
I agree it is compliant, and acceptable, but i would have charged £400 and used RCBO's, but that is down to the customer i suppose.
Cheers..........Howard
I priced a C/U change in a 1 bed flat with only 4 circuits (1 lighting) I phoned elecsa and they reckoned it was perfectly satisfactory to put in a single RCD board. I quoted £230 for this. The guys jaw nearly hit the floor, another firm had come in and quoted £750.
Another very happy customer.
I agree it is compliant, and acceptable, but i would have charged £400 and used RCBO's, but that is down to the customer i suppose.
Cheers..........Howard
Aye and I'd of got the job
I rarely even bother trying to suggest RCBO boards to people these days (I'll admit, I hate installing them) they usually look baffled enough when I try and explain what an RCD is and would rather pay £350 for something they don't understand or particulalry want (15 way board) than £600 for something they still dont understand and is no safer.
Hey lets do that then. i like doing consumer units/distribution boards. More circuits the merrier. makes it more of an interesting job!If you want to take this to the extreme then every room should have it’s own MCB. BUT a room may have a centre light and wall lights, so that’s two MCB’s. One step further and each room should have it’s own radial for the sockets. We will finish up with every house having to have Sizewell B switching station under the stairs.
My knob and tubes have always had a good polish in the States.
My knob is fine but my tubes don't work any longer since visiting the US!