sparkymatt1987

Can anyone help with estimating a dates of original installations. It needs recording on the certificates but can't come up with a date. What are the signs to look for to estimate a date. Other than rubber cables and old wooden backed wylex boards.
 
green cpc sleeving would date it pre early 70's. stranded cables about the same. a photo or 2 might help.
 
If im not sure i use the > button,, say old wylex poss rubber cables then greater than say 40 years. pvc but still looking old then >30 its an estimate remember, make it up.. its a pointless question
 
[TABLE="width: 471"]
[TR]
[TD]It is only an Esitmate at the end of the day! I had a really good guide but can't find it at the moment, but here's a few things:
10MM bonding cables - 80's or later (could have just been added later though!)[/TD]
[/TR]
[TR]
[TD]No main bonding - pre 1966[/TD]
[/TR]
[TR]
[TD]Supplementary bonding in place - 1981 or later[/TD]
[/TR]
[TR]
[TD]No cpc in lighting circuit - pre 1966[/TD]
[/TR]
[TR]
[TD]Green earth sleeving - pre 1977[/TD]
[/TR]
[TR]
[TD]Fuse in the neutral conductor - pre 1955[/TD]
[/TR]
[TR]
[TD]Voltage operated earth leack circuit breakers pre 1981[/TD]
[/TR]
[TR]
[TD]None square pinned 13A socket outlets - 50's and before[/TD]
[/TR]
[TR]
[TD]Red/Black cable colours - pre 2006[/TD]
[/TR]
[TR]
[TD]Imperial Twin & Earth - pre 1970[/TD]
[/TR]
[/TABLE]
 