Good evening all
Called out today to a rural bungalow where the decorator reported to the owner he had received an electric shock from the wall whilst sanding and refused to continue.
Installation consisted of TNC-S system, Wylex BS3036 rewire-able fuse box, no bonding to water or oil services, brass class1 socket outlets.
Carried out ZE 0.2 ohms
carried out Zs on socket outlet on suspect wall >2000
Isolated & removed cables at fuse box cpc proved open circuit.
Cable tracer transmitter connected at socket outlet and into the loft we go, traced fault to disconnected cpc in jb in loft.
Re-connected cpc & re-tested all ok
Customer has now given me the go ahead to replace fusebox & upgrade earth & bonding etc.
My question is as follows: -
If an electric shock was received surely that means that voltage/current was leaking to earth (if it had been in place)
Does this mean the new CU with RCD protection is likely to trip or is it normal for a small amount to leak to earth (obviously less than 30ma) and would this be enough to give an electrical shock?
All advice welcomed as always.
Thank you
Called out today to a rural bungalow where the decorator reported to the owner he had received an electric shock from the wall whilst sanding and refused to continue.
Installation consisted of TNC-S system, Wylex BS3036 rewire-able fuse box, no bonding to water or oil services, brass class1 socket outlets.
Carried out ZE 0.2 ohms
carried out Zs on socket outlet on suspect wall >2000
Isolated & removed cables at fuse box cpc proved open circuit.
Cable tracer transmitter connected at socket outlet and into the loft we go, traced fault to disconnected cpc in jb in loft.
Re-connected cpc & re-tested all ok
Customer has now given me the go ahead to replace fusebox & upgrade earth & bonding etc.
My question is as follows: -
If an electric shock was received surely that means that voltage/current was leaking to earth (if it had been in place)
Does this mean the new CU with RCD protection is likely to trip or is it normal for a small amount to leak to earth (obviously less than 30ma) and would this be enough to give an electrical shock?
All advice welcomed as always.
Thank you