H
Heisenberg
Thanks for the reply, BS7671 does not require circuits to be upgraded to current regulations to be connected to a replacement ccu, only for it to be ascertained that they are not an immediate danger (which I would read as no C1's or C2's), GN3 even says there is no obligation to inspect or test any part of the installation!
Also found this : www.niceic.com/Uploads/File1950.pdf Guidance on cu replacement, which also says the same. interesting reading.
The document you refer to also says this:
Where a consumer unit is being replaced, additional protection by means of RCDs in accordance with Regulation 415.1 should be provided to the extent required by the current edition BS 7671, such as for:
• socket-outlets (Regulation 411.3.3 refers),
• mobile equipment for use outdoors (Regulation 411.3.3 refers),
• cables concealed in walls or partitions, where required by Regulations 522.6.6 to 522.6.8, and
• circuits of locations containing a bath or shower (Regulation 701.411.3.3 refers).
So if you are changing the CU you need to use RCD/RCBOs. You can't just avoid putting that circuit on a RCCD because it keeps tripping. And sod what the customer says, it won't be him appearing in front of the men in funny wigs if it all goes south. Do it the way it's meant to be done or walk away, simples.