I'm being sent to look at a job where a colleague has replaced a dimmer that controls 2 wall lights three times. Apparently 40W candle lamps in pairs. I can think of no reason why this arrangement should keep taking the dimmer out.
Any ideas before I go there on Tuesday?
 
Clamp the outgoing line to the lights and see what current is being taken, it may be there is a fault on the lights overloading the dimmer.
You can get low load dimmers that only have a max rating of 100W, but it sounds unlikely to be that.
 
i think the o/p means that the dimmer has been replaced 3 times and is controlling 2 wall lights with 2X 40 watt lamps in each one which equals 160watts
 
i think the o/p means that the dimmer has been replaced 3 times and is controlling 2 wall lights with 2X 40 watt lamps in each one which equals 160watts
yes yes i know....i was just being facetious...
 
how can it be overheating it only got to dim a 160 watt load i reckon the op is taking the micky
 
Last edited by a moderator:
As per Richard clamp it, possibly its being inadvertantly expected to dim something else.

As in not a light
 