Doomed

~
Arms
May 26, 2009
1,048
776
688
Dorset
I'm being sent to look at a job where a colleague has replaced a dimmer that controls 2 wall lights three times. Apparently 40W candle lamps in pairs. I can think of no reason why this arrangement should keep taking the dimmer out.
Any ideas before I go there on Tuesday?
 
Clamp the outgoing line to the lights and see what current is being taken, it may be there is a fault on the lights overloading the dimmer.
You can get low load dimmers that only have a max rating of 100W, but it sounds unlikely to be that.
 
  • Like
Reactions: 1 person
i think the o/p means that the dimmer has been replaced 3 times and is controlling 2 wall lights with 2X 40 watt lamps in each one which equals 160watts
 
i think the o/p means that the dimmer has been replaced 3 times and is controlling 2 wall lights with 2X 40 watt lamps in each one which equals 160watts
yes yes i know....i was just being facetious...
 
how can it be overheating it only got to dim a 160 watt load i reckon the op is taking the micky
 
Last edited by a moderator:
As per Richard clamp it, possibly its being inadvertantly expected to dim something else.

As in not a light
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Doomed

Arms
~
Joined
Location
Dorset

Thread Information

Title
Dimmer blowing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Doomed,
Last reply from
SPARTYKUS,
Replies
11
Views
2,409

Advert