the theory behind it is L1 L2 L3 gives a clockwise phase rotation and it is a repeating pattern,

L1 L2 L3 L1 L2 L3 L1 L2 L3 and so on

so if you pick any 3 that are next to each other it will give clockwise rotation.
i.e L2 L3 L1 is still clockwise and so is L3 L1 L2
convention and simplicity means that we wire 1 2 3 but the other options will work the same.
I try tonight, make the example on empty page .
Just need to to be be careful motor is 400v.???
That asking for advice all day .
Thank you ...
 
The Forward Contactor will be the one with the Forward Start pushbutton wired to the N/O of that contact.
or if nothing is labelled up then:
As the Forward & Reverse circuits are functionally the same then just pick one for Forward and the other for Reverse. The actual Forward & Reverse wiring for the motor is not part of this circuit.
Can you asking for writing wires drawing please , should be easy .
Thank you .
 
Can you asking for writing wires drawing please , should be easy .
Thank you .

Sorry mate, I don't understand the question.
You already have the schematic, so I presume you don't want that again.
 
step by step is best. break each section down, understand the workings, then combine all together.
 
Ok , Easy wiring diagram but , I doing step by step .

Have a look at @telectrix post above, with the wiring diagram on it. That shows the wiring for the motor as well.
Also follow his advice about breaking the schematic into sections.
If you have any questions mate then just ask.
 
The Forward Contactor will be the one with the Forward Start pushbutton wired to the N/O of that contact.
or if nothing is labelled up then:
As the Forward & Reverse circuits are functionally the same then just pick one for Forward and the other for Reverse. The actual Forward & Reverse wiring for the motor is not part of this circuit.
Can you asking for writing wires dia
The Forward Contactor will be the one with the Forward Start pushbutton wired to the N/O of that contact.
or if nothing is labelled up then:
As the Forward & Reverse circuits are functionally the same then just pick one for Forward and the other for Reverse. The actual Forward & Reverse wiring for the motor is not part of this circuit.
[/QUOTE
Finally done last night.
Ok, so just so that I'm clear on this: You are just following the drawing and picture, to see how it works and not actually wiring anything up?
Finally done last night. Thank you for Help .59396A93-AD72-46DB-889D-EC4EE0E57348.jpeg
 
Glad you got it working mate.

If you want, now that it is working I'd tidy it up, label cables and use correct colour cables.
Just for general information, below is a screen shot of cable colour identification, from BS EN 60204-1-2018 (page 83)

1570695153393.png
 
I know , but I don’t like make new post .
I little be confused theory now , I not have proper book,Any idea where did I find examples test .
I’m ready too pay small amount ££££.
Pdf file .
Thank you .

Hi mate.
It's best if you do new questions in a new post mate.
Also, if you are going to get into electrical design then you need to get the BS7161 book.

Also, with questions like the above, we don't like giving out answers without you first attempting to do the question and showing us your workings-out. Then we can correct anything. It's the best way of learning.
 
It always looks intimidating @Zaprinski when it written like that but all the things you need are in bs 7671 just take your time and break the question down.....if you know your design current and installation method and relevant correction factors you can choose your cable and then you can calculate for volt drop, the more you do it the easier it gets...good luck
 
Hi mate.
It's best if you do new questions in a new post mate.
Also, if you are going to get into electrical design then you need to get the BS7161 book.

Also, with questions like the above, we don't like giving out answers without you first attempting to do the question and showing us your workings-out. Then we can correct anything. It's the best way of learning.
Ok I got book I try to work out and show you my home work .
Thank you for help .
 
Yes, I'd observed that. There should really be a N/C contact from each direction's contactor inhibiting the other direction's coil circuit. Wouldn't stop the operator hitting stop then reverse immediately - but it would stop them just hitting reverse.
Mind you, the mechanical interlock would deal with that - but IMO it would be poor design to be relying on that rather than designing the control circuit correctly.
 
Yes, I'd observed that. There should really be a N/C contact from each direction's contactor inhibiting the other direction's coil circuit. Wouldn't stop the operator hitting stop then reverse immediately - but it would stop them just hitting reverse.
Mind you, the mechanical interlock would deal with that - but IMO it would be poor design to be relying on that rather than designing the control circuit correctly.
Thank you .
 
Yes, I'd observed that. There should really be a N/C contact from each direction's contactor inhibiting the other direction's coil circuit.

There is. There is a N/C contact from the Reverse contactor in the Forward circuit and vice veras.
 

Reply to Direct online forwarding and reverse. in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
410
NICEIC Certification Scheme Getting accredited to
Looking for some advice regarding joining a CPS. I've been in the electrical industry in various roles for nearly 10 years. I started my...
Replies
15
Views
853
I recently sold my Renault Trafic as it had done 214,000 miles and I also wanted something more economical. I bought the Citroen Berlingo LWB. A...
Replies
34
Views
2K
Hi, sorry if this is the wrong place to ask, I am wondering about becoming an electrician of some form or another and thought to come to an...
Replies
15
Views
1K
Hi all, I'm currently training thru a company called tradestech, not very impressed so far, I was told that within 6 months I'd be able to...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock