Currently reading:
UK DIY. Hi Is a 2.5mm T+E cable ok for kitchen appliances ?

Discuss DIY. Hi Is a 2.5mm T+E cable ok for kitchen appliances ? in the UK Electrical Forum area at ElectriciansForums.net

Redmist

DIY
Reaction score
0
Hi My new extension has 2.5mm T+E cable running to the Hob. The hob needs replacing I have been advised that there should have been a minimum of 4mm cable running to the Hob to comply with part P of the building regs ?
Could you please clarify this for me.
many thanks
Wojtek
 
Is the T&E connected directly to the hob?

What circuit is the hob powered from sockets or on it's own circuit and do you know the MCB size for the circuit?

What's the rating of the hob?
 
Many thanks for your reply'
The hob is a Zanussi Induction hob 13 Amp supply.
it has its own circuit.
not sure about the other things.
Then on the face of it that's fine for the supply to the hob isolator. Most 13a appliances come already flexed, so I'm assuming that's the case here and the flex goes to the isolator. Or are you saying this is 2.5 T&E also.
Whatever, no need for 4mm, and it has nothing to do with part p.
 

Reply to DIY. Hi Is a 2.5mm T+E cable ok for kitchen appliances ? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top